Question about the adaptive level. I understand that when set according to 12464 the raster is according to the standard, but if I set adaptive and put a 2x2 step where the average comes out to over 600lx still in the results is 572lx. Can we please explain how this works then ? Thanks
Adaptive vs 12464
Adaptive vs 12464
Přemysl Tomšovic - Accredited trainer
Top osvětlení s.r.o.
https://www.top-osvetleni.cz
https://www.top-osvetleni.cz/sluzby/vypocty-osvetleni
https://www.top-osvetleni.cz/sluzby/mereni-osvetleni
Top osvětlení s.r.o.
https://www.top-osvetleni.cz
https://www.top-osvetleni.cz/sluzby/vypocty-osvetleni
https://www.top-osvetleni.cz/sluzby/mereni-osvetleni
Re: Adaptive vs 12464
Hello beta-pt,
Please provide us with the evo project file so that we can check the behaviour directly in evo 10.1. It would be of help if you could send us the link to this topic so that we could better assign this issue. Our email address is 'Support@dialux.com'.
Best regards,
DIAL Support Team
Please provide us with the evo project file so that we can check the behaviour directly in evo 10.1. It would be of help if you could send us the link to this topic so that we could better assign this issue. Our email address is 'Support@dialux.com'.
Best regards,
DIAL Support Team
-
- Posts: 1645
- Joined: Thu Jul 26, 2012 10:16 am
Re: Adaptive vs 12464
Hello beta-pt,
We forwarded your project file to our developers for analysis. We will get back in touch with you as soon as we get a feedback from them.
Best regards,
DIAL Support Team
We forwarded your project file to our developers for analysis. We will get back in touch with you as soon as we get a feedback from them.
Best regards,
DIAL Support Team
-
- Posts: 1645
- Joined: Thu Jul 26, 2012 10:16 am
Re: Adaptive vs 12464
Dear beta-pt,
In the result monitor, the result of the adaptive calculation (min, max, average) is also displayed. The "value chart settings" refer, as the name suggests, only to the "value chart", i.e. the graphical value grid. The settings have absolutely no influence on the results.
In particular, you do not set the number of calculation points, but only at how many points a value is displayed in the CAD.
If you want to have results neither according to EN-12464 grid nor adaptive, you have to insert a calculation surface and set the calculation grid accordingly. This is not possible on the working plane.
Best regards,
DIAL Support Team
In the result monitor, the result of the adaptive calculation (min, max, average) is also displayed. The "value chart settings" refer, as the name suggests, only to the "value chart", i.e. the graphical value grid. The settings have absolutely no influence on the results.
In particular, you do not set the number of calculation points, but only at how many points a value is displayed in the CAD.
If you want to have results neither according to EN-12464 grid nor adaptive, you have to insert a calculation surface and set the calculation grid accordingly. This is not possible on the working plane.
Best regards,
DIAL Support Team
Re: Adaptive vs 12464
Ok thanks
Přemysl Tomšovic - Accredited trainer
Top osvětlení s.r.o.
https://www.top-osvetleni.cz
https://www.top-osvetleni.cz/sluzby/vypocty-osvetleni
https://www.top-osvetleni.cz/sluzby/mereni-osvetleni
Top osvětlení s.r.o.
https://www.top-osvetleni.cz
https://www.top-osvetleni.cz/sluzby/vypocty-osvetleni
https://www.top-osvetleni.cz/sluzby/mereni-osvetleni
Who is online
Users browsing this forum: No registered users and 0 guests